Gainsborough stanza se 8.5

hi my shower is only giving out luke warm shower when turn right up on the red ,, can i change the engine to a 10.5 kw or would i have to change the shower completely
Asked 5 years ago by Andrew Simmonds, wales
Fitting a more powerful shower to the existing wiring.

If your existing shower was installed with 6mm wiring (as it should have been) then fitting another shower (even up to one of the 10kw units) to the existing wiring should be no problem, depending on the length of the run off cable and how the cable is installed.

Here is a table that allows you to work out what you can do with the existing wiring, make sure you fill it in accurately as this can make a large difference to the eventual calculation.

www.tlc-direct.co.uk/Technical/Charts/VoltageDrop.html

You may also have to change the fuse

Up to 8.5kw 35 Amp fuse

Up to 9.5kw 40 Amp Fuse

Up to 10.5kw 45 Amp Fuse

If you are even in the slightest unsure about any of the above then please contact an electrician.

Answered 5 years ago by Barrie Seabright

View Spares and Order Parts:

Do you need any additional help to find the correct spare part?

Please click the following link if you would like to see other answers or ask a question regarding the Gainsborough 10.5 SE - Shower Spares

If you've landed here and this question is not about your specific product, please take a look at these similar items on our Gainsborough Electric Showers Spares page. Alternatively, if you're looking for any other brands you should view our full range of Shower Spares.

If you do not want to proceed with a repair or you want to buy this item or similar, please consider one of our Replacement Gainsborough Electric Showers

For any other support request please get in touch.